Hello I have an issue with my basement sump pump (original by Mattamy, about 9 years old). It remains continuously ON, but not sucking water; only few drops are being pumped out. I originally thought it was due to too cold outside and possible there was no water in the structure. However, since the snow has melted considerably, that should not be the case. In any case, pump should turn off if there was no water.

What could be the issue?

Does anyone know a handy man who can replace pump for me?


Top
 Profile  
Reply with quote  
PostPosted: Mon Feb 04, 2019 10:40 pm 
Offline
User avatar

Joined: Tue Jan 31, 2012 11:42 pm
Posts: 1474
Unplug it, right now, do not let it run steadily until you fix it. You should be looking to replace that thing soon ideally.

Since it's so warm it will not be that the outlet is frozen. It ts stuck on somehow, most probably the float is hanging up or the switch is broken in the on position.

There is a ton of online content to read, in here as well as on YT. Also worth reading: https://www.google.ca/search?q=milton+f ... jwTw4K-gDQ

_________________
This one thing probably never goes away
I think this one thing is always supposed to stay
This one thing doesn't have to go away


Top
 Profile  
Reply with quote  
PostPosted: Tue Feb 05, 2019 8:14 am 
Offline
User avatar

Joined: Sun Jun 01, 2008 10:14 am
Posts: 4834
Location: Milton
Very wise advice B&T402. The sump needs to be unplugged. This problem can cause a fire in the pit that can result in significant damage to the home or worse. All one needs to do is the Google - Milton sump fires or Halton sump fires to see that this is a problem.

It could be a very simple problem that is easily fixed. Usually the float is stuck causing the pump switch to stay in the ON position OR the pump is just defective. Typically builders install low cost pumps in the homes they build and sometimes the installations are poorly done. Pedestal pumps have been the main cause of fires but poorly installed submersible pumps can also overheat. Either way, after nine years it is probably time for a new pump.

There are low cost pumps with plastic parts and plastic impellers and better cast iron pumps with steel impellers. People who think they will soon want to replace their pumps may want to keep an eye out for some great sales at TSC on good quality pumps.

_________________
For Home Inspection services call Andy Shaw at Halton Home Inspection Service. 905 876 4761


Top
 Profile  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 8 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group
[ Time : 0.011s | 13 Queries | GZIP : Off ]